General Category => Support Questions => Topic started by: Darrell on August 18, 2016, 07:41:41 PM

Title: Guage show wrong value
Post by: Darrell on August 18, 2016, 07:41:41 PM
Gauge  always seems to go to  full value using ver 399n  Micrologix 1400
Title: Re: Guage show wrong value
Post by: Archie on August 18, 2016, 08:33:52 PM
Add a BasicLabel next to the gage with PLCAddressValue set to the same address as the gage to show what the value should be.
Title: Re: Guage show wrong value
Post by: Darrell on August 18, 2016, 08:51:26 PM
Thanks, that is what I had done anyway , was just wondering , think it worked in earlier versions , not sure how fa back though

Darrell
Title: Re: Guage show wrong value
Post by: Archie on August 18, 2016, 09:41:00 PM
I was thinking to add the BasicLabel in order to see the real value is in the PLC because the tank does post processing on the value. I was going to try to replicate the values you have.
Title: Re: Guage show wrong value
Post by: Darrell on August 18, 2016, 10:01:01 PM
I think I know what was happening  , I was also using a seven digit display for the same PLC address with a number like 571 with a decimal place showing 57.1 but the same number in the gauge puts it over the scale max of 70  A scale factor of .1 would make it display within the range is this correct.

Sorry man, should have noticed this earlier
Darrell