General Category => Support Questions => Topic started by: Darrell on August 18, 2016, 07:41:41 PM
-
Gauge always seems to go to full value using ver 399n Micrologix 1400
-
Add a BasicLabel next to the gage with PLCAddressValue set to the same address as the gage to show what the value should be.
-
Thanks, that is what I had done anyway , was just wondering , think it worked in earlier versions , not sure how fa back though
Darrell
-
I was thinking to add the BasicLabel in order to see the real value is in the PLC because the tank does post processing on the value. I was going to try to replicate the values you have.
-
I think I know what was happening , I was also using a seven digit display for the same PLC address with a number like 571 with a decimal place showing 57.1 but the same number in the gauge puts it over the scale max of 70 A scale factor of .1 would make it display within the range is this correct.
Sorry man, should have noticed this earlier
Darrell