Im new to using this software, and Im trying to connect a bassicButton and a basicIndicator to boolean bits in the PLC. How do I address the button and indicator to the tags I have created in the PLC? Any help would be appreciated.
-
What PLC are you using?
-
I am using a Logix5561 using ethernet communication.
-
For the BasicButton, enter a controller scope Boolean tag into the PLCAddressClick property. For the BasicInidicator, also enter a controller scope Boolean tag into PLCAddressValue
-
There is no PLCAddressValue for the indicator and also when I put the tag name into the field for the button it tells me that it is an invalid tag name. It is possible I am typing it wrong.
-
Maybe take a screenshot of what you are setting. It sounds like you are in the wrong area.
-
There is no PLCAddressValue for the indicator.
Sorry, my mistake , the property is PLCAddressSelectColor2.
Are you sure it is a controller scope tag and not a program scope?
-
Archie, I had them as program tags and not controller tags. I switched them and it works fine now. Thanks!
-
It is possible to use program scope tags, but I always recommend starting with controller scope just to eliminate that extra layer. You can read about how to use program scope tags here:
http://advancedhmi.com/documentation/index.php?title=EthernetIPforCLXCom