Author Topic: Omron Host Link and getting started  (Read 2213 times)

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5269
    • View Profile
    • AdvancedHMI
Re: Omron Host Link and getting started
« Reply #15 on: May 22, 2018, 05:57:35 PM »
Change your processor from RUN to MONITOR mode

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5269
    • View Profile
    • AdvancedHMI
Re: Omron Host Link and getting started
« Reply #16 on: May 22, 2018, 06:01:48 PM »
Look at section 4-3-10 of the manual and you will see a table of Execution Conditions that shows you cannot write to the CIO using C-Mode commands while the processor is in Run Mode.

Ecoli-557

  • Newbie
  • *
  • Posts: 25
    • View Profile
Re: Omron Host Link and getting started
« Reply #17 on: May 22, 2018, 06:05:30 PM »
That did it!  AND the feedback of 0.0 also works.......
Will you explain the difference and will AHMI work with OmronSerialHostLink in RUN mode?

Ecoli-557

  • Newbie
  • *
  • Posts: 25
    • View Profile
Re: Omron Host Link and getting started
« Reply #18 on: May 22, 2018, 06:06:15 PM »
You just answered my question.

Ecoli-557

  • Newbie
  • *
  • Posts: 25
    • View Profile
Re: Omron Host Link and getting started
« Reply #19 on: May 22, 2018, 06:10:03 PM »
OK, Thanks again for pointing out that I have much more to digest....... <grin>.
I am trying to enable logging and it errors out saying Property Value is not valid.
Now what????

Ecoli-557

  • Newbie
  • *
  • Posts: 25
    • View Profile
Re: Omron Host Link and getting started
« Reply #20 on: May 23, 2018, 05:39:43 PM »
Hello, anyone?
I tried to Enable Logging on Omron Serial Host Link and I get this error:
Property Value is not valid.
I kinda need this logging to better understand what AHMI and the PLC is doing.