AdvancedHMI Software
General Category => Open Discussion => Topic started by: abdala on May 03, 2018, 11:20:22 AM
-
error modbus rtu and tcp
(http://a.up-00.com/2018/05/152536076752161.jpg)
-
What are those other errors you have in Immediate Window, prior to the error in your picture?
If you set this driver's DisableSubscriptions property to True and run the program, does the window show at all?
-
When the value changes, the program does not run
This problem exists even in previous versions
You have tried changing the value and the program does not work
-
If your program doesn't run when you set this driver's DisableSubscriptions property to True, it means that something else is not working properly.
Can you take a picture of Immediate Window errors (extend its size to fit all the errors)?
-
This error does not always come but it is present in all versions of the program
-
What is your Facebook account to communicate with you
-
I don't have a Facebook account.
This forum communication should be sufficient to help resolve the errors.
If you remove the driver all together from your project and the program still doesn't run then that should indicate problems with something else.
-
Here is a picture of the form that I just deleted all drivers from.
It still runs and the controls show the error.
-
Add ModbusRTUCom1 and you will see what song
DisableSubscriptions=true
Do not read
-
How to read timer in modbus rtu
-
What controls do you have on your form? There is a control that is subscribing prior to OnCreateControl. You could begin deleting controls until the error goes away to see which one is the culprit.
-
ok Thank
How to read timer in modbus rtu
-
Timers typically map to a 4000 series address
-
It seems that the company PLC ls has improved communication
modbus rtu and tcp
I am using now
Example:
TMR 1=4001
Try it now on PLC LS XGB does not work
read D0 NOT TIMR 0
-
Thanks for finding the solution to the problem of reading the Taimer