This is the second machine that was upgraded from an old PanelView 1000 to AdvancedHMI. This one used the AdvancedHMI 15" Panel PC

https://www.advancedhmi.com/index.php?main_page=product_info&cPath=1&products_id=16

Part of the upgrade was to add a wireless access point and a tablet for maintenance to setup the machine.

The machine uses a ControlLogix (L63 processor) with a combination of Ethernet/IP and DeviceNet IO. The program was so large it was taking 120-200ms to scan the program. Also part of the upgrade was to go update to an 1756-L85E processor. This brought the scan time down to 7ms and the HMI was re-configured to refresh at 50ms which made a huge difference in HMI response.

bachphi:
impressive scan time going from L63 to L85. Any changes to System Overhead Time Slice??

Phrog30:
With the 8 series, you generally don't have to worry about timeslice since communications has it's own processor.

dmroeder:
With the L8x, there actually is no overhead system time slice.  That configuration has been removed for reasons Phrog30 mentioned.

Darrell:
would love to see that program