Title: Modbus TCP flowmeters
Post by: frank222 on August 12, 2019, 05:46:37 PM
Good afternoon
I have a flowmeter and I need to send the totalized data to a data base, the communication is modbus tcp, I cannot read the data, please if someone can help me addressing, I attach the manual thanks

Modbus register 152
Modbus address 151
No. of bytes   2
Data type      Float
Description   Float TOTAL
Read/ Write    R
Title: Re: Modbus TCP flowmeters
Post by: Archie on August 12, 2019, 05:55:47 PM
F40152

or

40152@F with version 3.99y
Title: Re: Modbus TCP flowmeters
Post by: frank222 on August 14, 2019, 06:25:25 PM
Archie thanks for answering
It is a flowmeter that has a Lantronix port 10001 brand Ethernet port card installed, a port other than 502 can be used because I cannot receive the flowmeter data.
Title: Re: Modbus TCP flowmeters
Post by: Archie on August 15, 2019, 11:18:27 AM
It is a flowmeter that has a Lantronix port 10001 brand Ethernet port card installed, a port other than 502 can be used because I cannot receive the flowmeter data.
Do you mean the TCP Port as set in the driver instance?
Title: Re: Modbus TCP flowmeters
Post by: frank222 on August 15, 2019, 04:36:22 PM
ok Archie
Title: Re: Modbus TCP flowmeters
Post by: frank222 on August 28, 2019, 09:41:03 AM
Hello Archie
The flowmeter protocol is modus rtu over TCP, there will be some possibility of achieving communication through AdvancedHMI
Thanks