Im having troubles with my dc inputs on my 1100 plc looking for an address for these 2 on board 10 volt inputs that works
ive tried them all but the right one signed frustrated lol
-
You might get a little help from the manual:
http://literature.rockwellautomation.com/idc/groups/literature/documents/rm/1763-rm001_-en-p.pdf
or possibly somebody who has the same PLC.
-
Rockwell can send a man to the moon sometimes but they cant give you a straight answer as to addressing there I/0 im not pulse modulating it or nothing fancy just feeding o-10 volts to it im just looking for an address .its on the main cpu so it should start with
I: OR I. TRIED THEM / SOMETHING TRIED THE MANUAL?
-
hopeful,
From my reading of the manual for which Godra posted the link it seems that these should be as follows:
1) I:0.0
2) I:0.1
For the two onboard analog inputs.
Doug Lyons
-
this input I:0.0 SHOULD GO TO A FLOATING POINT TO VIEW?
-
I FOUND IT IT WAS ACTUALLY I:0.4 I don't know but it works thanks??!!! newbies rock
-
thanks doug
-
Hope this reply is not to late.
I:0.0 is the digital inpupts of the PLC.
I:0.4 is the first analog and I:0.5 the second.
Both analogs are 0-10VDC and the PLC returns an integer from 0 to 1023
Beware not override 10.5V on inputs, will permenant damage occur.
Hope to be usefull