Reading and displaying Real formats
« on: December 19, 2018, 06:09:54 AM »
I am getting real values in a database from a siemens S7 1200 PLC which is configured as as Modbus TCP server. Each value occupies 2 modbus registers. When I choose register 40001for example I am getting a displayed value which is far beyond the actual. Can you help me configure it properly? I set number of element as 2.

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5269
    • View Profile
    • AdvancedHMI
Re: Reading and displaying Real formats
« Reply #1 on: December 19, 2018, 07:00:02 AM »
You need to use what is referred to as address modifers:

F40001

or 40001@F in the latest beta version


https://www.advancedhmi.com/forum/index.php?topic=765.0