General Category => Support Questions => Topic started by: Yvan on November 16, 2015, 03:47:29 PM
-
I'm just trying to get started by creating a simple "hello world" program.
My PLC is programmed so that when input 20 goes high, output 16 goes high (a lights an indicator).
In AdvancedHMI, I have a button and an indicator. The button's PLCAddressClick is set to _IO_EM_DI_20 and the indicator's PLCAddressSelectColor2 is set to _IO_EM_DO_16.
I have also tried using aliases (SENSOR/LED_WHITE) and traditional addressing (I1:20) etc.
When I click the button I get CIP Error Path destination unknown. Manually setting I20 high does not colour the indicator (but it does light my LED).
Thanks for your help.
-
Try to create a BOOL tag (controller scope) without the leading "_", then use that tag name in PLCAddressSelectColor2
The Micro800 has some restrictions on reading certain tags and maybe it will not allow the tag you are trying to use
-
It looks like my problem was that I was addressing the I/Os directly. I created a global variable and used that instead, and copied its value to the I/O in the PLC and it worked. Thanks!