General Category => Feature Request => Topic started by: MrPike on May 17, 2018, 10:23:53 PM
-
Is it possible to to modify the basic label to read strings from modbus thru the property settings? I know that I can write the code to do this but was wondering if it can be a default function where i can enter the starting register and number of consecutive reads and whamo, the string displays in the basiclabel text. I ask because i plan to use a bunch of them and want to avoid writing the code. Thanks.
-
The latest beta version of 3.99y supports strings in the Modbus driver. The address modifiers have been changed to accommodate this. You can now use an address like 40001@S10 to read 10 bytes starting at 40001 and it returns the result in the format of a string. So you can put that address in the BasicLabel's property of PLCAddressValue.
You can get the beta version from here:
https://www.advancedhmi.com/forum/index.php?topic=2058.0
-
That's awesome Archie! What is the easiest way to upgrade from 3.99x? Thank you.
-
Archie, I started migrating my project from 3.99x to 3.99y by adding the .vb files as existing items. Everything went well until I got these errors. There are a bunch more than shown. What I noticed is all my AHMI components are now missing. I have the drivers but no controls. I shut VS and restarted but no luck. How do I proceed? Thank you
-
To do an upgrade:
- Download and extract the latest version
- Open the latest in Visual Studio
- In Solution Explorer right click the AdvancedHMI project and select Add->Existing Item
- Browse to your old solution
- Select one of the *.vb files that corresponds to each form (e.g. MainForm.vb) Only select 1 at a time and repeat for each form otherwise it will not pull the associated files in with it
- Once all of the forms are imported to the new version, Build the solution
- You may get a few errors in places where property names have changed. Double click each error and manually correct
-
I recommend putting everything unique to you in a separate folder. It makes upgrading A LOT easier.
-
I worked thru this. I had followed the steps you outlined but I think the issue came about when I deleted your mainform to add my mainform. The entire .dll file for the drivers was missing. I copied the .dll file from a fresh copy and it cleared most of my errors. BTW, the Modbus string read feature works like a champ in the latest version. Thank you.