Good morning, I am doing some Float register readings in modbus TCP and I am using the AnalogoValueDisplay with PlcAddressValue F40001. It reads correctly the float register, taking register 40002 as the most significant register (where the sign and the exponent are), I wonder how I could do it the other way round, that is, with register 40001 as the most significant register.
Thank you very much
-
In the Modbus driver, try to set SwapWords to True to see if that does what you want.
-
Yes! i just test It. As always thank you!!