I have connected my Click PLC to the AHMI and can read / write to everything I need to except floating point addresses.
I have tried to word swap, byte swap and both to no avail..
I can write to an address (i.e. 428691) and it changes the number, but not to the number I entered.
I am assuming I have not configured something correctly, but I can't figure out my mistake.
Any help would be appreciated

Thank you,

Dean

rbelknap

  • Jr. Member
  • **
  • Posts: 68
    • View Profile
Re: Click PLC Floating point addressing problem
« Reply #1 on: January 08, 2016, 07:46:16 AM »
I assume you're using the Modbus driver.

Try Putting and "F" in front of the address.

See this thread by Archie for explanation:
http://advancedhmi.com/forum/index.php?topic=765.0

nis

  • Newbie
  • *
  • Posts: 2
    • View Profile
Re: Click PLC Floating point addressing problem
« Reply #2 on: January 09, 2016, 12:19:38 AM »
Thank you for the reply.  That did the trick!!