AdvancedHMI Software
General Category => Support Questions => Topic started by: Ismael on January 23, 2018, 09:44:33 AM
-
Hola
Cómo se puede leer un registro de 32 bits con el display digital. Tengo un plc omron y tengo un número en los registros D100 y D101 . Cómo se configura el componente en el advance para que me lea esa palabra.
-
For those who search the forum for specific words, this would be a Google translation:
How can a 32-bit register be read with the digital display. I have an Omron PLC and I have a number in the D100 and D101 registers. How to configure the component in advance to read that word.
-
This requires the patched version that can be downloaded here (it is AdvancedHMIV399xPatched3.zip):
https://sourceforge.net/projects/advancedhmi/files/advancedhmi/3.5/
Then you would use an address modifier like this:
D100@L
-
ya descargué la aplicación pero cuando agrego los componentes y los ejecuto no apararecen en la simulación.
"I already downloaded the application but when I add the components and execute them, they do not appear in the simulation"
-
Are you editing the ManForm.vb in the AdvancedHMI project?
-
si ya estoy editando, el plc me muestra comunicación, pero el digital meter no muestra valor ni escribiendo D100.
-
Are you using serial or Ethernet? If using serial, is your CX-Programmer completely shutdown so AdvancedHMI can get access to the serial port?
-
La AdvancedHMIv399x.zip me trabaja solo en 16 bits.
AdvancedHMIV399xPatched3.zip no me está trabajando.