Hello,
I am trying to develop a communication between an ABB PM581 CPU and AdvancedHMI thought Modbus. Currently i am able to read a variable defined in memory but i can't write it with the panelmeter keypad option.

I am also having problems reading Inputs and writing Outputs directly, i have to assign them to a memory variable in the PLC program and read/write trought that variable. Which is the correct Modbus address?

Has anybody made a good communication with this PLC(Or another ABB) using Modbus?

Thank you very much.

P.D.: This is the definition of all variables in Codesys:
          VAR_GLOBAL
                      Inputs AT %IW0: WORD;
                      Outputs AT %QW0: WORD;
                      Mem1 AT %MW0.0: WORD;
                      Mem2 AT %MW0.1: WORD;
         END_VAR

Friedrich

  • Newbie
  • *
  • Posts: 19
    • View Profile
Re: ABB AC500 and Modbus Communication
« Reply #1 on: May 16, 2015, 05:29:54 PM »
Finally got around to playing with the AC500 (PM554) and AdvancedHMI (3.98g). I found this document: http://www402.abbext.com/DownloadFile.aspx?file=UserFiles/Answers201308/ABB-Ac500-Modbus.pdf&filename=ABB-Ac500-Modbus.pdf
To start with; You cannot read or write to I/O directly. You have to assign the variables to memory, just like you found out the hard way.

I played around with some bits and words and got it working after some headscratching. Here's the global variable list I set up with comments which function codes/addresses works:

VAR_GLOBAL
   Bit0 AT %MX0.0.0 : BOOL; (* Read: 10001 - Write: 00001 *)
   Bit1 AT %MX0.0.1 : BOOL; (* Read: 10002 - Write: 00002 *)
   Bit2 AT %MX0.0.2 : BOOL; (* Read: 10003 - Write: 00003 *)
   Bit3 AT %MX0.0.3 : BOOL; (* Read: 10004 - Write: 00004 *)
   Bit4 AT %MX0.0.4 : BOOL; (* Read: 10005 - Write: 00005 *)
   Bit5 AT %MX0.0.5 : BOOL; (* Read: 10006 - Write: 00006 *)
   Bit6 AT %MX0.0.6 : BOOL; (* Read: 10007 - Write: 00007 *)
   Bit7 AT %MX0.0.7 : BOOL; (* Read: 10008 - Write: 00008 *)
   Word0 AT %MW0.0 : WORD; (* Read & write: 40001 *)
   Word1 AT %MW0.1 : WORD; (* Read & write: 40002 *)
   Word2 AT %MW0.2 : WORD; (* Read & write: 40003 *)
   Word3 AT %MW0.3 : WORD; (* Read & write: 40004 *)
END_VAR

Note that the bits are from the first word. The funny thing is that I couldn't write bits or words with any of the intended function codes.
Just take a look at the document I linked for the mapping of the memory. Note that the addressing is completely wrong in it.