General Category => Support Questions => Topic started by: calimero100582 on December 15, 2015, 10:40:58 AM
-
Hi
I have a CompactLogix with a Custom type wich I call CustomTimer containing Delay, and Count, both integer
I also have a CustomTimers array of 10 elements of type CustomTimer
I can read and write using CustomTimers[1].Delay, but when I try to simply read CustomTimers as an array, I got Driver Exception saying "No Response from PLC"
Is there an easy way to read/write such arrays, or I really need to scan all values one by one?
Thanks
-
You can only read atomic data types. The driver would not know how to return a UDT.
The next version will let you read UDTs, but they will only be returned as an array of bytes that you would have to write code to reassemble.
-
Thanks, I hope will be able to Write data also.
For my current issue, I'll have to do some check with a newer/current version of ADHMI
With an older version (3.68) I had issue with send queue full when writing large arrays or multiple values at once, and I had to add a Sleep between every Write (see: http://advancedhmi.com/forum/index.php?topic=444.msg1769#msg1769)
I updated AdvancedHMI to 3.99a, but I've not tested performance with it, and I am still using a Thread.Sleep between every Write
As I have a couple of arrays like my CustomTimers, I don't want to wait between every Write. I'll do some test to see if I still need the Sleep, as the Write is my main concern in this case, and for the moment I only have 20 values to write, but I expect to have more than 1000 values to write at once.
-
The changes in 3.99a made all writes synchronous so you will not have to use sleeps.
-
Hey Archie,
Even I'm using UDT with 3.99a version Is there a easy way around.
-
My workaround was to use an equivalent class in C# with .net reflection I loop through property and read every property from a base tag