I'm testing AHMI to use on our plant floor. I'm not experienced with VB. The PLC is a Micro850. I'm using the EthernetIPforMicro800Com driver.
I'm trying a basic tag read and write HMI with a button and a label using the Properties / PLC Properties dialogue. I can read / write to the 1 dimensional array SensorGPM[1] without a problem. I can read / write to the 2 dimensional array Recipe[1,1].
Trying to read / write to the 2 dimensional array Recipe[RecipeSelect,1] results in invalid tag name. Both tags a global. I must have the formatting wrong, can someone please help me out?
Thanks
-
I assume RecipeSelect is a tag in the PLC. The PLC cannot decipher tags embedded into another.
You must first read the value of RecipeSelect, then use that value
Dim RecipeSelectValue as string = EthernetIPforCLXCom1.Read("RecipeSelect")
Dim RecipeValue as string = EthernetIPforCLXCom1.Read("Recipe[" & RecipeSelectValue & ",1]")
-
Thank you, I can see the pattern now.