HMI button to PLC tag
«
on:
July 27, 2017, 04:21:41 PM »
Im new to using this software, and Im trying to connect a bassicButton and a basicIndicator to boolean bits in the PLC. How do I address the button and indicator to the tags I have created in the PLC? Any help would be appreciated.
Logged
Archie
Administrator
Hero Member
Posts: 5365
Re: HMI button to PLC tag
«
Reply #1 on:
July 27, 2017, 05:14:19 PM »
What PLC are you using?
Logged
dmoore26
Newbie
Posts: 4
Re: HMI button to PLC tag
«
Reply #2 on:
July 27, 2017, 07:33:52 PM »
I am using a Logix5561 using ethernet communication.
Logged
Archie
Administrator
Hero Member
Posts: 5365
Re: HMI button to PLC tag
«
Reply #3 on:
July 27, 2017, 07:38:37 PM »
For the BasicButton, enter a controller scope Boolean tag into the PLCAddressClick property. For the BasicInidicator, also enter a controller scope Boolean tag into PLCAddressValue
Logged
dmoore26
Newbie
Posts: 4
Re: HMI button to PLC tag
«
Reply #4 on:
July 27, 2017, 08:39:19 PM »
There is no PLCAddressValue for the indicator and also when I put the tag name into the field for the button it tells me that it is an invalid tag name. It is possible I am typing it wrong.
Logged
Phrog30
Guest
Re: HMI button to PLC tag
«
Reply #5 on:
July 27, 2017, 08:49:48 PM »
Maybe take a screenshot of what you are setting. It sounds like you are in the wrong area.
Logged
Archie
Administrator
Hero Member
Posts: 5365
Re: HMI button to PLC tag
«
Reply #6 on:
July 27, 2017, 08:52:40 PM »
Quote from: dmoore26 on July 27, 2017, 08:39:19 PM
There is no PLCAddressValue for the indicator.
Sorry, my mistake , the property is PLCAddressSelectColor2.
Are you sure it is a controller scope tag and not a program scope?
Logged
dmoore26
Newbie
Posts: 4
Re: HMI button to PLC tag
«
Reply #7 on:
July 28, 2017, 08:04:34 AM »
Archie, I had them as program tags and not controller tags. I switched them and it works fine now. Thanks!
Logged
Archie
Administrator
Hero Member
Posts: 5365
Re: HMI button to PLC tag
«
Reply #8 on:
July 28, 2017, 08:09:08 AM »
It is possible to use program scope tags, but I always recommend starting with controller scope just to eliminate that extra layer. You can read about how to use program scope tags here:
http://advancedhmi.com/documentation/index.php?title=EthernetIPforCLXCom
Logged