Author Topic: Read failed status code -20  (Read 12584 times)

kf4ozb

  • Newbie
  • *
  • Posts: 16
    • View Profile
Read failed status code -20
« on: July 17, 2013, 11:16:12 AM »
Hiya Archie,

I have a form that has approximately 24 Comboboxes on it that I am populating using the new ReadSynchronous function (Which to this point seems to have fixed the previous sequence numbers being returned, Great job to those who contributed to the fix! ).  That being said I do seem to be getting a lot of read failures that return a value of -20.  I doubt this has anything to do with the new function.  More likely it's due to my network.

I traced this back to the WaitForResponse function.  Basically, if I understand the function, you are waiting for 1 second for a response.  If no response is received you return the error value of -20.

My questions are. What network topology was the current MaxTicks value optimized for?  Do you have an algorithm for determining a value based on different topologies?

Thanks again!

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5365
    • View Profile
    • AdvancedHMI
Re: Read failed status code -20
« Reply #1 on: July 17, 2013, 06:40:21 PM »
Do you also have other controls on the form that is displaying data? It seems that too many requests can go to the PLC and it begins to ignore some of them.

I can't test this right now, but this is something to try. In the driver code, find the PollUpdate subroutine. In that subroutine, there is a call to ReadAny. Try changing that to ReadSynchronous

kf4ozb

  • Newbie
  • *
  • Posts: 16
    • View Profile
Re: Read failed status code -20
« Reply #2 on: July 18, 2013, 03:13:07 PM »
I'm not using a control to read the information. I'm using the ReadSynchronus function.  However; I do have it in a for loop with no delay,( other than the processing time it takes to iterate through the loop).  I will try adding a sleep at the end of the for loop to give the PLC some breathing room and report back the results.

Do you have any recommendations for the time spacing between requests?

Thanks,

Mickey

Here is the code:

 Dim t As String
        Dim Read As Boolean

        For i = 0 To 23
            Read = False
            While Not Read
                Try
                    't = frm_csMain.EthernetIPforCLXComm1.ReadAny(Formula_List(i))

                    t = frm_csMain.EthernetIPforCLXComm1.ReadSynchronous(Formula_List(i), 1)(0) ' Updated to ReadSynchronus as bug fix from Advanced HMI 3.4
                    If t = "$00$00$00$00$00$00$00$00$00$00" Then t = ""
                    If isFormulaValid(t, CompoundNumber) Then   'Check to see if formula read is a vaild formula
                        Read = True
                        If t <> "" Then                         'If Valid and set disable control
                            With ControlArray(i)
                                .Enabled = False
                                .SelectedText = t
                            End With

                        Else
                            ControlArray(i).Enabled = True
                        End If
                    End If

                Catch ex As Exception
                    MsgBox(ex.ToString)
                    Exit For
                End Try

''''''ADDING THIS TO SEE IF IT FIXES THE ISSUE'''''''
               Sleep (100)
''''''END ADDITION'''''''

            End While


        Next

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5365
    • View Profile
    • AdvancedHMI
Re: Read failed status code -20
« Reply #3 on: July 18, 2013, 03:26:50 PM »
Just by nature, the ReadSynchronous waits until a response in received before returning from the cal, therefore a delay should not be needed.

One thing to keep in mind about Synchronous reading is that your operator interface will be unresponsive during your read loop.

Is this loop the only read that is occurring? Do you possibly have other forms that are open that could be reading at the same time?

kf4ozb

  • Newbie
  • *
  • Posts: 16
    • View Profile
Re: Read failed status code -20
« Reply #4 on: July 18, 2013, 03:57:04 PM »
Hmm.  Well now that you mention it. My main form stays visible and it has about 14 indicators on it, that would continue to poll the system.  If I disable the subscriptions to the communications driver, it should stop the advancedHMI components from polling the plc. Correct?  Can you still make ReadSynchronous calls 'manually' with the subscriptions disabled, or do I need to use another driver on my sub form?

Thanks for the input!

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5365
    • View Profile
    • AdvancedHMI
Re: Read failed status code -20
« Reply #5 on: July 18, 2013, 04:17:10 PM »
If you DisableSubscriptions on your driver, you can still do read and writes in your own code. Maybe the thing to try is to DisableSubscriptions when your read loop starts, then re-enable them after it is complete.

kf4ozb

  • Newbie
  • *
  • Posts: 16
    • View Profile
Re: Read failed status code -20
« Reply #6 on: July 18, 2013, 04:29:10 PM »
That's what I was thinking.  I'll try that and report back.

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5365
    • View Profile
    • AdvancedHMI
Re: Read failed status code -20
« Reply #7 on: July 19, 2013, 01:52:50 PM »
I did some quick testing on version 3.41 with 5 BasicLabels on a form with a PollRateOverride of 10ms. I then put a 20ms timer that read a single value followed by an array of 200 DINT. It ran for a few hours without a single miss in reading.

That version is now posted on sourceforge. If you get a chance, try it out to see if it resolves your issue.

kf4ozb

  • Newbie
  • *
  • Posts: 16
    • View Profile
Re: Read failed status code -20
« Reply #8 on: July 24, 2013, 10:14:03 AM »
Archie,

I was setting up a spare PLC to test this program on and I accidentally stumbled across a condition that causes this read failed status code -20 EVERY time.  Apparently, if you try to read an address with ReadSynchronous that does not exist this error is thrown.  I'm looking through your components now to see how you handle tags that do not exist. 

I don't know if this is the root cause of the -20 error that I've been experiencing.  I don't really think that it is, because if it were I would receive this error every time I clicked the schedule button, which runs my code. 

I'll let you know what else I find.

kf4ozb

  • Newbie
  • *
  • Posts: 16
    • View Profile
Re: Read failed status code -20
« Reply #9 on: July 24, 2013, 12:03:44 PM »
Ok.. I understand now why I'm getting -20 instead of the error the tag is invalid.  I went through the EthernetIPforCLXComm source and found that in the Subroutine 'DataLinkLayer_DataReceived'  a comparison is made to see if the data received was an internal request.  A ReadSynchronus call is sent with the InternalRequest property set to false.

The code that is being run when this occurs is below:

            '*****************************
            '* Failed Status was returned
            '*****************************
            Dim d() As String = {DecodeMessage(StatusByte) & " CIP Status " & StatusByte}
            If Not PLCAddressByTNS(e.TransactionNumber And 255).InternalRequest Then
                If Not DisableEvent Then
                    Dim x As New MfgControl.AdvancedHMI.Drivers.Common.PlcComEventArgs(d, PLCAddressByTNS(e.TransactionNumber And 255).TagName, e.TransactionNumber And 255)
                    If m_SynchronizingObject IsNot Nothing Then
                        Dim Parameters() As Object = {Me, x}
                        m_SynchronizingObject.BeginInvoke(drsd, Parameters) 

                    Else
                        'TODO : This should raise the Com Error event
                        RaiseEvent DataReceived(Me, x)
                    End If
                End If
            Else
                For i As Integer = 0 To SubscriptionList.Count - 1
                    If SubscriptionList(i).PLCAddress.TagName = PLCAddressByTNS(e.TransactionNumber And 255).TagName Then
                        m_SynchronizingObject.BeginInvoke(SubscriptionList(i).dlgCallBack, New Object() {d})
                    End If
                Next
            End If

The lines in Green are the code that is being evaluated when I receive the -20 error. Ultimately, it seems to me different information is returned when the request is external vs an internal request.   The question is then, how do I get a more detailed reason of why the read failed?  Can this be done just by making the Internal Request Property True?


Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5365
    • View Profile
    • AdvancedHMI
Re: Read failed status code -20
« Reply #10 on: July 24, 2013, 08:28:06 PM »
Is this still happening with the version 3.41?

The internalRequest is used to indicate that it is a read for updating subscriptions. The main difference is that it will send the resulting data out to the subscriptions, which in turn updates the controls.


kf4ozb

  • Newbie
  • *
  • Posts: 16
    • View Profile
Re: Read failed status code -20
« Reply #11 on: July 25, 2013, 08:50:43 AM »
It's happening with 3.41. I have not seen this error using basic labels or any other components.  It only occurs when I'm using a ReadSyncrhonous, and previous to the update a ReadAny call.  I have seen these components display "Error getting Tag" and then eventually populate data though.

The frequency varies. I've had instances where I get the error multiple times back to back, and other instances where only one error occurs.  As stated previously I stumbled accross a way to cause the error every single time the read is called, simply try to read a tag that does not exist.  (i.e. Me.EthernetIPforCLXComm1.ReadSynchronous("aHMI_ROCKS", 1)(0) cause the -20 error if "aHMI_ROCKS" is not defined in the PLC)  I don't think this is the cause of the intermittent -20 error I'm experiencing, because the error is intermittent and if you try to read a non-existent tag it fails continuously.

I believe the components are designed with some error decoding and handling that you don't get when you just use a read command.  Which is fine, if I know how to decode these errors and subsequently handle them.

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5365
    • View Profile
    • AdvancedHMI
Re: Read failed status code -20
« Reply #12 on: July 25, 2013, 10:27:22 AM »
I suspect what is happening is the reads from multiple driver instances are sending more commands than the controller can process.

If you have a MainForm with BasicLabels being updated and another form that you are calling the ReadSynchronous in code, try to reference the driver instance on the MainForm

MainForm.EthernetIPforCLXComm1.ReadSynchronous("MyTag",1)(0)

That way everything will channel through the same instance and be better regulated in sending the requests to the PLC.

Or you could hide the MainForm and it will stop the read updates to the BasicLabels.

kf4ozb

  • Newbie
  • *
  • Posts: 16
    • View Profile
Re: Read failed status code -20
« Reply #13 on: July 25, 2013, 11:11:00 AM »
That's what I'm doing.  I only have the one driver. I just change it's IP to read from different PLC's.

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5365
    • View Profile
    • AdvancedHMI
Re: Read failed status code -20
« Reply #14 on: July 25, 2013, 12:02:25 PM »
I am running out of ideas since I cannot replicate it on my setup. If you want, you can send me your project along with your RSLogix program. You can strip out all of the ladder code because I would only need the tags.

I do have a version 3.5.1 that is not ready for release. It should get around this problem. Maybe this weekend I can release part of it as an alpha version for you to test out.